Just a bit of context, I am a technology enthusiast. I love everything from software to hardware, Windows to Linux, Computer to Phone, and everything in between. So, I wouldn't be surprised is my electrical usage exceeds 50% of the entire household (8 people). To power all of the equipment I use, I use a pretty expensive surge protector, with 12 outlets on it. Recently, I have been very plain and simply, running out of outlets.
I have an extension cord with 3 outlets on it. Maybe, I thought, I could plug some of the things on my surge protector into the extension cord, and then the extension cord into the surge protector. I know, it's pretty dumb of me, but I went and did it, without checking to see if it was safe first. But I did, and everything seems to running fine. It's been running for about a 30 minutes now, and neither the surge protector or the extension cord are overheating.
However, after the fact, I am reading on websites about weather or not this is safe, and they're all saying it's not, even though everything is running perfectly fine. Thoughts? Something I'm not understanding?
safety surge-protection outlet overheat
New contributor
$endgroup$
add a comment |
$begingroup$
Just a bit of context, I am a technology enthusiast. I love everything from software to hardware, Windows to Linux, Computer to Phone, and everything in between. So, I wouldn't be surprised is my electrical usage exceeds 50% of the entire household (8 people). To power all of the equipment I use, I use a pretty expensive surge protector, with 12 outlets on it. Recently, I have been very plain and simply, running out of outlets.
I have an extension cord with 3 outlets on it. Maybe, I thought, I could plug some of the things on my surge protector into the extension cord, and then the extension cord into the surge protector. I know, it's pretty dumb of me, but I went and did it, without checking to see if it was safe first. But I did, and everything seems to running fine. It's been running for about a 30 minutes now, and neither the surge protector or the extension cord are overheating.
However, after the fact, I am reading on websites about weather or not this is safe, and they're all saying it's not, even though everything is running perfectly fine. Thoughts? Something I'm not understanding?
safety surge-protection outlet overheat
New contributor
$endgroup$
$begingroup$
The danger (if there is any) is that something will overheat and fail or start a fire. Since you are a technology enthusiast, you simply MUST have a thermal imaging camera or thermal imaging adapter for your mobile phone. Use this to make sure none of your cables or power strips are getting too warm. If they aren't, then most likely, all is well. If anything is getting hot, then take steps to reduce the load on it, or at least investigate further. It may take things a long time to reach their final temperature.
$endgroup$
– mkeith
28 secs ago
add a comment |
$begingroup$
Just a bit of context, I am a technology enthusiast. I love everything from software to hardware, Windows to Linux, Computer to Phone, and everything in between. So, I wouldn't be surprised is my electrical usage exceeds 50% of the entire household (8 people). To power all of the equipment I use, I use a pretty expensive surge protector, with 12 outlets on it. Recently, I have been very plain and simply, running out of outlets.
I have an extension cord with 3 outlets on it. Maybe, I thought, I could plug some of the things on my surge protector into the extension cord, and then the extension cord into the surge protector. I know, it's pretty dumb of me, but I went and did it, without checking to see if it was safe first. But I did, and everything seems to running fine. It's been running for about a 30 minutes now, and neither the surge protector or the extension cord are overheating.
However, after the fact, I am reading on websites about weather or not this is safe, and they're all saying it's not, even though everything is running perfectly fine. Thoughts? Something I'm not understanding?
safety surge-protection outlet overheat
New contributor
$endgroup$
Just a bit of context, I am a technology enthusiast. I love everything from software to hardware, Windows to Linux, Computer to Phone, and everything in between. So, I wouldn't be surprised is my electrical usage exceeds 50% of the entire household (8 people). To power all of the equipment I use, I use a pretty expensive surge protector, with 12 outlets on it. Recently, I have been very plain and simply, running out of outlets.
I have an extension cord with 3 outlets on it. Maybe, I thought, I could plug some of the things on my surge protector into the extension cord, and then the extension cord into the surge protector. I know, it's pretty dumb of me, but I went and did it, without checking to see if it was safe first. But I did, and everything seems to running fine. It's been running for about a 30 minutes now, and neither the surge protector or the extension cord are overheating.
However, after the fact, I am reading on websites about weather or not this is safe, and they're all saying it's not, even though everything is running perfectly fine. Thoughts? Something I'm not understanding?
safety surge-protection outlet overheat
safety surge-protection outlet overheat
New contributor
New contributor
New contributor
asked 1 hour ago
Ethan WaldeckEthan Waldeck
83
83
New contributor
New contributor
$begingroup$
The danger (if there is any) is that something will overheat and fail or start a fire. Since you are a technology enthusiast, you simply MUST have a thermal imaging camera or thermal imaging adapter for your mobile phone. Use this to make sure none of your cables or power strips are getting too warm. If they aren't, then most likely, all is well. If anything is getting hot, then take steps to reduce the load on it, or at least investigate further. It may take things a long time to reach their final temperature.
$endgroup$
– mkeith
28 secs ago
add a comment |
$begingroup$
The danger (if there is any) is that something will overheat and fail or start a fire. Since you are a technology enthusiast, you simply MUST have a thermal imaging camera or thermal imaging adapter for your mobile phone. Use this to make sure none of your cables or power strips are getting too warm. If they aren't, then most likely, all is well. If anything is getting hot, then take steps to reduce the load on it, or at least investigate further. It may take things a long time to reach their final temperature.
$endgroup$
– mkeith
28 secs ago
$begingroup$
The danger (if there is any) is that something will overheat and fail or start a fire. Since you are a technology enthusiast, you simply MUST have a thermal imaging camera or thermal imaging adapter for your mobile phone. Use this to make sure none of your cables or power strips are getting too warm. If they aren't, then most likely, all is well. If anything is getting hot, then take steps to reduce the load on it, or at least investigate further. It may take things a long time to reach their final temperature.
$endgroup$
– mkeith
28 secs ago
$begingroup$
The danger (if there is any) is that something will overheat and fail or start a fire. Since you are a technology enthusiast, you simply MUST have a thermal imaging camera or thermal imaging adapter for your mobile phone. Use this to make sure none of your cables or power strips are getting too warm. If they aren't, then most likely, all is well. If anything is getting hot, then take steps to reduce the load on it, or at least investigate further. It may take things a long time to reach their final temperature.
$endgroup$
– mkeith
28 secs ago
add a comment |
3 Answers
3
active
oldest
votes
$begingroup$
To be honest, I do it all the time. However, there are some things to keep in mind:
- Never exceed the maximum power, current and voltage.
- Voltage will normally not be a problem since this is (more or less) stable in a country. When you go abroad, check if they can be used.
- current is most important, sum up all devices you connect on that extension cord AND all devices on extension connected to the the first extension cord. Take some margin, especially motors sometimes can use a lot of 'starting' current.
- Don't forget when you switch on an extension cord (either by plugging it in, or by using a switch if there is on), ALL devices will be powered on at the same time, using possibly some additional extra current.
- When you go towards the maximum current supported by the extension cord, make sure the cable is fully unrolled (meaning not bundled), since warmth cannot spread.
$endgroup$
add a comment |
$begingroup$
If you only plug low current devices into the extension cord there should be no problem. In any case, you need to keep the total current requirements of everthing plugged into the surge protector and extension cord below the rating of the surge protector. You also must consider the current requirement of anything else on the same circuit as the outlet the surge protector is pluggged into.
Manufacturers warn against plugging extensions or other power bars into a surge protector in case someone plugs a 15 amp heater into the last of three power bars.
$endgroup$
add a comment |
$begingroup$
I'll add some information to what Michael and Peter wrote in their good answers.
You are right about lots of warnings being written everywhere on the subject. This is some sort of scarecrow tactic from the manufacturers (and rightly so, IMO).
Manufacturers must design their product and the included instructions around the (possibly dumbest) average consumer. Average people, sadly, have very little understanding of how electricity works: they confuse power, voltage and current all the time, let alone knowing what Ohm's law or Joule's law are!
So manufacturers don't take any chances. They tell you the simplest possible rule to use their products with safety: "One extension cord (adapter plug, or whatever) to one socket, no multiple adapter/extension things joined together". Stop. Simple and hopefully foolproof.
Of course, extension cords, plugs, sockets and similar "electrical connection things" follow Ohm's law and Joule's law. This latter is particularly important to calculate heating. If you know what you are doing and know the characteristics of your loads, you can mix and match almost anything by providing generous safety margins.
I have been running various multiple extension cords setups for ages, without the slightest problem. "Normal" people could watch my setups and cower in terror (if they are sane), or they could do the same and burn their house down, because they can't tell the electrical difference between a 4W power pack and a 1500W toaster! :-D
$endgroup$
add a comment |
Your Answer
StackExchange.ifUsing("editor", function () {
return StackExchange.using("mathjaxEditing", function () {
StackExchange.MarkdownEditor.creationCallbacks.add(function (editor, postfix) {
StackExchange.mathjaxEditing.prepareWmdForMathJax(editor, postfix, [["\$", "\$"]]);
});
});
}, "mathjax-editing");
StackExchange.ifUsing("editor", function () {
return StackExchange.using("schematics", function () {
StackExchange.schematics.init();
});
}, "cicuitlab");
StackExchange.ready(function() {
var channelOptions = {
tags: "".split(" "),
id: "135"
};
initTagRenderer("".split(" "), "".split(" "), channelOptions);
StackExchange.using("externalEditor", function() {
// Have to fire editor after snippets, if snippets enabled
if (StackExchange.settings.snippets.snippetsEnabled) {
StackExchange.using("snippets", function() {
createEditor();
});
}
else {
createEditor();
}
});
function createEditor() {
StackExchange.prepareEditor({
heartbeatType: 'answer',
autoActivateHeartbeat: false,
convertImagesToLinks: false,
noModals: true,
showLowRepImageUploadWarning: true,
reputationToPostImages: null,
bindNavPrevention: true,
postfix: "",
imageUploader: {
brandingHtml: "Powered by u003ca class="icon-imgur-white" href="https://imgur.com/"u003eu003c/au003e",
contentPolicyHtml: "User contributions licensed under u003ca href="https://creativecommons.org/licenses/by-sa/3.0/"u003ecc by-sa 3.0 with attribution requiredu003c/au003e u003ca href="https://stackoverflow.com/legal/content-policy"u003e(content policy)u003c/au003e",
allowUrls: true
},
onDemand: true,
discardSelector: ".discard-answer"
,immediatelyShowMarkdownHelp:true
});
}
});
Ethan Waldeck is a new contributor. Be nice, and check out our Code of Conduct.
Sign up or log in
StackExchange.ready(function () {
StackExchange.helpers.onClickDraftSave('#login-link');
});
Sign up using Google
Sign up using Facebook
Sign up using Email and Password
Post as a guest
Required, but never shown
StackExchange.ready(
function () {
StackExchange.openid.initPostLogin('.new-post-login', 'https%3a%2f%2felectronics.stackexchange.com%2fquestions%2f423697%2fis-it-safe-to-plug-an-extension-cord-into-a-power-strip%23new-answer', 'question_page');
}
);
Post as a guest
Required, but never shown
3 Answers
3
active
oldest
votes
3 Answers
3
active
oldest
votes
active
oldest
votes
active
oldest
votes
$begingroup$
To be honest, I do it all the time. However, there are some things to keep in mind:
- Never exceed the maximum power, current and voltage.
- Voltage will normally not be a problem since this is (more or less) stable in a country. When you go abroad, check if they can be used.
- current is most important, sum up all devices you connect on that extension cord AND all devices on extension connected to the the first extension cord. Take some margin, especially motors sometimes can use a lot of 'starting' current.
- Don't forget when you switch on an extension cord (either by plugging it in, or by using a switch if there is on), ALL devices will be powered on at the same time, using possibly some additional extra current.
- When you go towards the maximum current supported by the extension cord, make sure the cable is fully unrolled (meaning not bundled), since warmth cannot spread.
$endgroup$
add a comment |
$begingroup$
To be honest, I do it all the time. However, there are some things to keep in mind:
- Never exceed the maximum power, current and voltage.
- Voltage will normally not be a problem since this is (more or less) stable in a country. When you go abroad, check if they can be used.
- current is most important, sum up all devices you connect on that extension cord AND all devices on extension connected to the the first extension cord. Take some margin, especially motors sometimes can use a lot of 'starting' current.
- Don't forget when you switch on an extension cord (either by plugging it in, or by using a switch if there is on), ALL devices will be powered on at the same time, using possibly some additional extra current.
- When you go towards the maximum current supported by the extension cord, make sure the cable is fully unrolled (meaning not bundled), since warmth cannot spread.
$endgroup$
add a comment |
$begingroup$
To be honest, I do it all the time. However, there are some things to keep in mind:
- Never exceed the maximum power, current and voltage.
- Voltage will normally not be a problem since this is (more or less) stable in a country. When you go abroad, check if they can be used.
- current is most important, sum up all devices you connect on that extension cord AND all devices on extension connected to the the first extension cord. Take some margin, especially motors sometimes can use a lot of 'starting' current.
- Don't forget when you switch on an extension cord (either by plugging it in, or by using a switch if there is on), ALL devices will be powered on at the same time, using possibly some additional extra current.
- When you go towards the maximum current supported by the extension cord, make sure the cable is fully unrolled (meaning not bundled), since warmth cannot spread.
$endgroup$
To be honest, I do it all the time. However, there are some things to keep in mind:
- Never exceed the maximum power, current and voltage.
- Voltage will normally not be a problem since this is (more or less) stable in a country. When you go abroad, check if they can be used.
- current is most important, sum up all devices you connect on that extension cord AND all devices on extension connected to the the first extension cord. Take some margin, especially motors sometimes can use a lot of 'starting' current.
- Don't forget when you switch on an extension cord (either by plugging it in, or by using a switch if there is on), ALL devices will be powered on at the same time, using possibly some additional extra current.
- When you go towards the maximum current supported by the extension cord, make sure the cable is fully unrolled (meaning not bundled), since warmth cannot spread.
answered 1 hour ago
Michel KeijzersMichel Keijzers
6,35492866
6,35492866
add a comment |
add a comment |
$begingroup$
If you only plug low current devices into the extension cord there should be no problem. In any case, you need to keep the total current requirements of everthing plugged into the surge protector and extension cord below the rating of the surge protector. You also must consider the current requirement of anything else on the same circuit as the outlet the surge protector is pluggged into.
Manufacturers warn against plugging extensions or other power bars into a surge protector in case someone plugs a 15 amp heater into the last of three power bars.
$endgroup$
add a comment |
$begingroup$
If you only plug low current devices into the extension cord there should be no problem. In any case, you need to keep the total current requirements of everthing plugged into the surge protector and extension cord below the rating of the surge protector. You also must consider the current requirement of anything else on the same circuit as the outlet the surge protector is pluggged into.
Manufacturers warn against plugging extensions or other power bars into a surge protector in case someone plugs a 15 amp heater into the last of three power bars.
$endgroup$
add a comment |
$begingroup$
If you only plug low current devices into the extension cord there should be no problem. In any case, you need to keep the total current requirements of everthing plugged into the surge protector and extension cord below the rating of the surge protector. You also must consider the current requirement of anything else on the same circuit as the outlet the surge protector is pluggged into.
Manufacturers warn against plugging extensions or other power bars into a surge protector in case someone plugs a 15 amp heater into the last of three power bars.
$endgroup$
If you only plug low current devices into the extension cord there should be no problem. In any case, you need to keep the total current requirements of everthing plugged into the surge protector and extension cord below the rating of the surge protector. You also must consider the current requirement of anything else on the same circuit as the outlet the surge protector is pluggged into.
Manufacturers warn against plugging extensions or other power bars into a surge protector in case someone plugs a 15 amp heater into the last of three power bars.
answered 1 hour ago
Peter BennettPeter Bennett
37.5k12968
37.5k12968
add a comment |
add a comment |
$begingroup$
I'll add some information to what Michael and Peter wrote in their good answers.
You are right about lots of warnings being written everywhere on the subject. This is some sort of scarecrow tactic from the manufacturers (and rightly so, IMO).
Manufacturers must design their product and the included instructions around the (possibly dumbest) average consumer. Average people, sadly, have very little understanding of how electricity works: they confuse power, voltage and current all the time, let alone knowing what Ohm's law or Joule's law are!
So manufacturers don't take any chances. They tell you the simplest possible rule to use their products with safety: "One extension cord (adapter plug, or whatever) to one socket, no multiple adapter/extension things joined together". Stop. Simple and hopefully foolproof.
Of course, extension cords, plugs, sockets and similar "electrical connection things" follow Ohm's law and Joule's law. This latter is particularly important to calculate heating. If you know what you are doing and know the characteristics of your loads, you can mix and match almost anything by providing generous safety margins.
I have been running various multiple extension cords setups for ages, without the slightest problem. "Normal" people could watch my setups and cower in terror (if they are sane), or they could do the same and burn their house down, because they can't tell the electrical difference between a 4W power pack and a 1500W toaster! :-D
$endgroup$
add a comment |
$begingroup$
I'll add some information to what Michael and Peter wrote in their good answers.
You are right about lots of warnings being written everywhere on the subject. This is some sort of scarecrow tactic from the manufacturers (and rightly so, IMO).
Manufacturers must design their product and the included instructions around the (possibly dumbest) average consumer. Average people, sadly, have very little understanding of how electricity works: they confuse power, voltage and current all the time, let alone knowing what Ohm's law or Joule's law are!
So manufacturers don't take any chances. They tell you the simplest possible rule to use their products with safety: "One extension cord (adapter plug, or whatever) to one socket, no multiple adapter/extension things joined together". Stop. Simple and hopefully foolproof.
Of course, extension cords, plugs, sockets and similar "electrical connection things" follow Ohm's law and Joule's law. This latter is particularly important to calculate heating. If you know what you are doing and know the characteristics of your loads, you can mix and match almost anything by providing generous safety margins.
I have been running various multiple extension cords setups for ages, without the slightest problem. "Normal" people could watch my setups and cower in terror (if they are sane), or they could do the same and burn their house down, because they can't tell the electrical difference between a 4W power pack and a 1500W toaster! :-D
$endgroup$
add a comment |
$begingroup$
I'll add some information to what Michael and Peter wrote in their good answers.
You are right about lots of warnings being written everywhere on the subject. This is some sort of scarecrow tactic from the manufacturers (and rightly so, IMO).
Manufacturers must design their product and the included instructions around the (possibly dumbest) average consumer. Average people, sadly, have very little understanding of how electricity works: they confuse power, voltage and current all the time, let alone knowing what Ohm's law or Joule's law are!
So manufacturers don't take any chances. They tell you the simplest possible rule to use their products with safety: "One extension cord (adapter plug, or whatever) to one socket, no multiple adapter/extension things joined together". Stop. Simple and hopefully foolproof.
Of course, extension cords, plugs, sockets and similar "electrical connection things" follow Ohm's law and Joule's law. This latter is particularly important to calculate heating. If you know what you are doing and know the characteristics of your loads, you can mix and match almost anything by providing generous safety margins.
I have been running various multiple extension cords setups for ages, without the slightest problem. "Normal" people could watch my setups and cower in terror (if they are sane), or they could do the same and burn their house down, because they can't tell the electrical difference between a 4W power pack and a 1500W toaster! :-D
$endgroup$
I'll add some information to what Michael and Peter wrote in their good answers.
You are right about lots of warnings being written everywhere on the subject. This is some sort of scarecrow tactic from the manufacturers (and rightly so, IMO).
Manufacturers must design their product and the included instructions around the (possibly dumbest) average consumer. Average people, sadly, have very little understanding of how electricity works: they confuse power, voltage and current all the time, let alone knowing what Ohm's law or Joule's law are!
So manufacturers don't take any chances. They tell you the simplest possible rule to use their products with safety: "One extension cord (adapter plug, or whatever) to one socket, no multiple adapter/extension things joined together". Stop. Simple and hopefully foolproof.
Of course, extension cords, plugs, sockets and similar "electrical connection things" follow Ohm's law and Joule's law. This latter is particularly important to calculate heating. If you know what you are doing and know the characteristics of your loads, you can mix and match almost anything by providing generous safety margins.
I have been running various multiple extension cords setups for ages, without the slightest problem. "Normal" people could watch my setups and cower in terror (if they are sane), or they could do the same and burn their house down, because they can't tell the electrical difference between a 4W power pack and a 1500W toaster! :-D
answered 24 mins ago
Lorenzo DonatiLorenzo Donati
16.8k44476
16.8k44476
add a comment |
add a comment |
Ethan Waldeck is a new contributor. Be nice, and check out our Code of Conduct.
Ethan Waldeck is a new contributor. Be nice, and check out our Code of Conduct.
Ethan Waldeck is a new contributor. Be nice, and check out our Code of Conduct.
Ethan Waldeck is a new contributor. Be nice, and check out our Code of Conduct.
Thanks for contributing an answer to Electrical Engineering Stack Exchange!
- Please be sure to answer the question. Provide details and share your research!
But avoid …
- Asking for help, clarification, or responding to other answers.
- Making statements based on opinion; back them up with references or personal experience.
Use MathJax to format equations. MathJax reference.
To learn more, see our tips on writing great answers.
Sign up or log in
StackExchange.ready(function () {
StackExchange.helpers.onClickDraftSave('#login-link');
});
Sign up using Google
Sign up using Facebook
Sign up using Email and Password
Post as a guest
Required, but never shown
StackExchange.ready(
function () {
StackExchange.openid.initPostLogin('.new-post-login', 'https%3a%2f%2felectronics.stackexchange.com%2fquestions%2f423697%2fis-it-safe-to-plug-an-extension-cord-into-a-power-strip%23new-answer', 'question_page');
}
);
Post as a guest
Required, but never shown
Sign up or log in
StackExchange.ready(function () {
StackExchange.helpers.onClickDraftSave('#login-link');
});
Sign up using Google
Sign up using Facebook
Sign up using Email and Password
Post as a guest
Required, but never shown
Sign up or log in
StackExchange.ready(function () {
StackExchange.helpers.onClickDraftSave('#login-link');
});
Sign up using Google
Sign up using Facebook
Sign up using Email and Password
Post as a guest
Required, but never shown
Sign up or log in
StackExchange.ready(function () {
StackExchange.helpers.onClickDraftSave('#login-link');
});
Sign up using Google
Sign up using Facebook
Sign up using Email and Password
Sign up using Google
Sign up using Facebook
Sign up using Email and Password
Post as a guest
Required, but never shown
Required, but never shown
Required, but never shown
Required, but never shown
Required, but never shown
Required, but never shown
Required, but never shown
Required, but never shown
Required, but never shown
$begingroup$
The danger (if there is any) is that something will overheat and fail or start a fire. Since you are a technology enthusiast, you simply MUST have a thermal imaging camera or thermal imaging adapter for your mobile phone. Use this to make sure none of your cables or power strips are getting too warm. If they aren't, then most likely, all is well. If anything is getting hot, then take steps to reduce the load on it, or at least investigate further. It may take things a long time to reach their final temperature.